Let me start this log by saying that what you will see here is actually about 20 different projects all rolled up into a single multi-year infrastructure overhaul. When I started at this school district there was no money for anything. Technology infrastructure had been neglected for several years as the district had never had an engineer on staff. Below you will find pictures and descriptions of this over-haul now that it has been completed. I have been compiling these pictures over the past several years once I knew the upgrades were going to happen. Some of the pictures will look better than others as several different cameras were used during different phases.
Smaller projects that did not require special certifications (i.e. HVAC, Electrical) I completed in-house with my own staff. Vendors would be called in to take care of special sections such as upgrading an electrical panel, etc. For our very large projects we brought in a VAR that provided us the manpower necessary while I project managed.

The west side of our district office MDF. These are the earliest pictures I have of the room when I began working here. By this time I had already cleaned up a little from what it originally looked like on my first day. There were boxes piled up in front of the door so high that you couldn’t open the door all the way. There were UPS units that were brand new in the box that had been sitting there for 2 years.
From left to right. Our NEC PBX system. There is an even older PBX chassis sitting on the floor that does nothing but condition the power for the NEC MUX. Next is our MUX and power conditioners. Also some marine batteries on the bottom. Then our CSU/DSU’s for the voice T-1’s to each school. Below them are monitors for a security system that no one is sure ever actually worked.
After the walkway gap is our Cisco 4500 and routers. The next 2 racks are all district servers. This is prior to any virtualization. Finally peaking in on the right is our Qwest MUX for the T3 that delivers 2 T1’s for our PRI’s.

The east side of the district office MDF. By this time I had already been able to get some new APC cabinets in to prepare the room for all the projects that were to come. You can also see 2 HVAC mini split units on the south wall. Each one is a Fujitsu 2 ton 19 SEER ductless unit. The room originally had a single 2 ton ceiling unit that was about 5 years old that had never been maintained. It was never able to keep the room under 80 degree even though it ran 24/7. These new units keep the room right at 72 degrees and we run them lead lag. Every quarter I switch them.

The north east corner of the district office MDF. What you are looking at is our Qwest fiber demark for both our Metro Optical WAN, and the T3 for the PRI’s. In the center is a 100 amp single phase panel that provides power for the receptacles in the room. On the right is a 100 amp 3-phase disconnect for the main UPS unit in the room. It is a APC Symetra 8Kva N+1 unit sitting on the floor.

The first phase of cleanup in the district office MDF. You see our Qwest fiber MUX has been removed to reveal the APC Symetra on the floor. We were also able to get rid of some of the 2 post racks as most of the servers were re-racked inside the APC Cabinets. Originally this room used to be 100% carpet. They came in at some point in time and ripped it up and laid PVC tile, however they skipped anything that had stuff in front of it, thus you see the ugly carpet spots.

More cleanup. The east wall shelves have been removed. We also put the UPS on a rolling dolly so we can move it around. Some of the carpet has been ripped up to finish the floor for Phase 1. The west side of the room will remain carpet until Phase 2.

west side of the room pre phase 1.

One of the important things we needed to do was move our fiber demarc to a different location in the room to allow us to install some other equipment where the demarc used to be. Once the Qwest MUX was removed we were able to terminate our T3 contract which saved about $15k per year. We moved our PRI’s over to copper. Since Qwest gets all agitated when you touch their equipment (and because I told them unless they send people I was going to move it myself) they were nice enough to send a crew to move the fiber.

Their 3 man crew made short work of it. In and out in about 45 minutes.

The Fujitsu units going up.

The north wall. All the electrical Panduit conduit has been removed to make way for wall repair and paint. HVAC remotes seen on the right.

A/C unit compressors on the outside of the MDF. There wasn’t enough room in the caged area to put them side by side so the HVAC guys built a double decker holder out of unistrut. Rather novel solution in my opinion.

Our maintenance department laying new PVC tile for us. Took a month of pestering him, but when he started it only took about 20 minutes.

Phase 1 PVC tile laid prior to sealing and waxing. I was worried when the new tile was such a contrast to the old tile, but the maintenance guys assured me once they stripped and waxed it I wouldn’t be able to tell where the new tile was.

Phase 1 stripped and waxed. They were right! You can’t even tell. Initial ladder rack on the left.

Next is electrical upgrades in the district office MDF. We had an electrician come out because we were getting rid of the Symetra and putting in newer units. It required the 3-phase disconnect to be switched out to a panel (load center). We also took the opportunity to demo the single phase panel. The new 3 phase panel will provide all the power for the room.

The 3 phase 480v sub panel that our new panel was coming off of. This panel was a direct connection back to the main for the building. We had to shut half the building down during this part because the old electrician that wired up the 3phase disconnect didn’t pull in a neutral. We also found out that they had wired the Symetra’s 3rd phase as the neutral. A BIG no no.

Inside shot of the 3 phase disconnect that was going away. You are seeing a fuse for each phase.

3phase disconnect and single phase panel now gone, new 3 phase panel going in. He is wiring up our new dual 8Kva UPS’s. Each unit is a dedicated 50amp single phase. And they aren’t sitting on the floor this time.

Circuits wired up and ready for load.

New 3 phase panel complete and turned on. The flex you see coming out of the top and bottom is temporary. Phase 2 will bring permanent outlets.
District Office MDF Phase 1 complete.
Will post more in the next few days.
Smaller projects that did not require special certifications (i.e. HVAC, Electrical) I completed in-house with my own staff. Vendors would be called in to take care of special sections such as upgrading an electrical panel, etc. For our very large projects we brought in a VAR that provided us the manpower necessary while I project managed.

The west side of our district office MDF. These are the earliest pictures I have of the room when I began working here. By this time I had already cleaned up a little from what it originally looked like on my first day. There were boxes piled up in front of the door so high that you couldn’t open the door all the way. There were UPS units that were brand new in the box that had been sitting there for 2 years.
From left to right. Our NEC PBX system. There is an even older PBX chassis sitting on the floor that does nothing but condition the power for the NEC MUX. Next is our MUX and power conditioners. Also some marine batteries on the bottom. Then our CSU/DSU’s for the voice T-1’s to each school. Below them are monitors for a security system that no one is sure ever actually worked.
After the walkway gap is our Cisco 4500 and routers. The next 2 racks are all district servers. This is prior to any virtualization. Finally peaking in on the right is our Qwest MUX for the T3 that delivers 2 T1’s for our PRI’s.

The east side of the district office MDF. By this time I had already been able to get some new APC cabinets in to prepare the room for all the projects that were to come. You can also see 2 HVAC mini split units on the south wall. Each one is a Fujitsu 2 ton 19 SEER ductless unit. The room originally had a single 2 ton ceiling unit that was about 5 years old that had never been maintained. It was never able to keep the room under 80 degree even though it ran 24/7. These new units keep the room right at 72 degrees and we run them lead lag. Every quarter I switch them.

The north east corner of the district office MDF. What you are looking at is our Qwest fiber demark for both our Metro Optical WAN, and the T3 for the PRI’s. In the center is a 100 amp single phase panel that provides power for the receptacles in the room. On the right is a 100 amp 3-phase disconnect for the main UPS unit in the room. It is a APC Symetra 8Kva N+1 unit sitting on the floor.

The first phase of cleanup in the district office MDF. You see our Qwest fiber MUX has been removed to reveal the APC Symetra on the floor. We were also able to get rid of some of the 2 post racks as most of the servers were re-racked inside the APC Cabinets. Originally this room used to be 100% carpet. They came in at some point in time and ripped it up and laid PVC tile, however they skipped anything that had stuff in front of it, thus you see the ugly carpet spots.

More cleanup. The east wall shelves have been removed. We also put the UPS on a rolling dolly so we can move it around. Some of the carpet has been ripped up to finish the floor for Phase 1. The west side of the room will remain carpet until Phase 2.

west side of the room pre phase 1.

One of the important things we needed to do was move our fiber demarc to a different location in the room to allow us to install some other equipment where the demarc used to be. Once the Qwest MUX was removed we were able to terminate our T3 contract which saved about $15k per year. We moved our PRI’s over to copper. Since Qwest gets all agitated when you touch their equipment (and because I told them unless they send people I was going to move it myself) they were nice enough to send a crew to move the fiber.

Their 3 man crew made short work of it. In and out in about 45 minutes.

The Fujitsu units going up.

The north wall. All the electrical Panduit conduit has been removed to make way for wall repair and paint. HVAC remotes seen on the right.

A/C unit compressors on the outside of the MDF. There wasn’t enough room in the caged area to put them side by side so the HVAC guys built a double decker holder out of unistrut. Rather novel solution in my opinion.

Our maintenance department laying new PVC tile for us. Took a month of pestering him, but when he started it only took about 20 minutes.

Phase 1 PVC tile laid prior to sealing and waxing. I was worried when the new tile was such a contrast to the old tile, but the maintenance guys assured me once they stripped and waxed it I wouldn’t be able to tell where the new tile was.

Phase 1 stripped and waxed. They were right! You can’t even tell. Initial ladder rack on the left.

Next is electrical upgrades in the district office MDF. We had an electrician come out because we were getting rid of the Symetra and putting in newer units. It required the 3-phase disconnect to be switched out to a panel (load center). We also took the opportunity to demo the single phase panel. The new 3 phase panel will provide all the power for the room.

The 3 phase 480v sub panel that our new panel was coming off of. This panel was a direct connection back to the main for the building. We had to shut half the building down during this part because the old electrician that wired up the 3phase disconnect didn’t pull in a neutral. We also found out that they had wired the Symetra’s 3rd phase as the neutral. A BIG no no.

Inside shot of the 3 phase disconnect that was going away. You are seeing a fuse for each phase.

3phase disconnect and single phase panel now gone, new 3 phase panel going in. He is wiring up our new dual 8Kva UPS’s. Each unit is a dedicated 50amp single phase. And they aren’t sitting on the floor this time.

Circuits wired up and ready for load.

New 3 phase panel complete and turned on. The flex you see coming out of the top and bottom is temporary. Phase 2 will bring permanent outlets.
District Office MDF Phase 1 complete.
Will post more in the next few days.